Here’s the scenario, 400amp delta(high leg) 3ph service already existing. Metering is through CTS at the top of the pole.
Service disconnect, no high leg identification, no neutral to EGC bond. All most be done at down stream panels because I have continuity between the two.
The main feeders go into a big junction box that from there feeds other panels out in the field which I have not seen.
Our job was to tap into the existing feeders to supply a new garage building (industrial).
I seen the guys that terminated our installed 200amp fused disconnect had bonded the neutral and EGC. As I noticed I figured that wasn’t right because we were downstream of the service disconnect, but after opening it and finding there was no bond, I left the bond in our disconnect for the feeders suppling the building.
Service disconnect, no high leg identification, no neutral to EGC bond. All most be done at down stream panels because I have continuity between the two.
The main feeders go into a big junction box that from there feeds other panels out in the field which I have not seen.
Our job was to tap into the existing feeders to supply a new garage building (industrial).
I seen the guys that terminated our installed 200amp fused disconnect had bonded the neutral and EGC. As I noticed I figured that wasn’t right because we were downstream of the service disconnect, but after opening it and finding there was no bond, I left the bond in our disconnect for the feeders suppling the building.