An unlicensed, unpermitted person who does not understand circuitry used a 10-2NM cable to wire a clothes dryer. I have recreated this circuit to study why it caused a fire.
At the circuit breaker panel, the black and white conductors were wired to the 2-30 breaker and the bare was wired to the ground bar.
In the 3 wire with ground dryer receptacle they wired black to black, white to white, and green to green. The fourth terminal, usually for the red conductor, was not connected to anything.
At the dryer terminals the 3 wire with ground dryer cord was wired black to black, white to white, green to the terminal that normally receives the red conductor, and red to nothing. The bonding jumper from the white terminal to the dryer casing was left in place.
Voltage at the dryer shows 240VAC black to white, 120VAC black to green, 120VAC white to green, 240VAC black to dryer casing, 0VAC white to dryer casing, 120VAC green to dryer casing.
Whether the dryer is running or not, you do not get shocked when you touch the dryer casing, but you do get shocked when you touch the dryer vent.
When the dryer is running, an ammeter shows 11 amps on the black, 5.3 amps on the white, and 10 amps on the green. An ammeter also shows 10 amps on the black and white inside the same CT, 11 amps on the white and green inside the same CT, and 5.2 amps on the black and green inside the same CT.
When the dryer is not running an ammeter shows 0 on all conductors.
The dryer motor and heater worked for 3-4 days before it started a fire. It is not known if the dryer was in use when the fire started.
The fire pattern seems to show that the fire started at the circuit breaker panel, not at or near the dryer, but the building was so badly damaged that it remains unknown.
The new flexible foil dryer vent may have been combined with an existing aluminum bath fan vent. The bath fan was properly wired and vented by a master electrician 12 years ago.
Can anyone help me determine why it took 3 to 4 days for this wiring to start a fire? And why it appears that the fire may have started at the circuit breaker panel, not at the dryer?
The fire had a tragic affect on my family. I am a master electrician. Thanks, TAH
At the circuit breaker panel, the black and white conductors were wired to the 2-30 breaker and the bare was wired to the ground bar.
In the 3 wire with ground dryer receptacle they wired black to black, white to white, and green to green. The fourth terminal, usually for the red conductor, was not connected to anything.
At the dryer terminals the 3 wire with ground dryer cord was wired black to black, white to white, green to the terminal that normally receives the red conductor, and red to nothing. The bonding jumper from the white terminal to the dryer casing was left in place.
Voltage at the dryer shows 240VAC black to white, 120VAC black to green, 120VAC white to green, 240VAC black to dryer casing, 0VAC white to dryer casing, 120VAC green to dryer casing.
Whether the dryer is running or not, you do not get shocked when you touch the dryer casing, but you do get shocked when you touch the dryer vent.
When the dryer is running, an ammeter shows 11 amps on the black, 5.3 amps on the white, and 10 amps on the green. An ammeter also shows 10 amps on the black and white inside the same CT, 11 amps on the white and green inside the same CT, and 5.2 amps on the black and green inside the same CT.
When the dryer is not running an ammeter shows 0 on all conductors.
The dryer motor and heater worked for 3-4 days before it started a fire. It is not known if the dryer was in use when the fire started.
The fire pattern seems to show that the fire started at the circuit breaker panel, not at or near the dryer, but the building was so badly damaged that it remains unknown.
The new flexible foil dryer vent may have been combined with an existing aluminum bath fan vent. The bath fan was properly wired and vented by a master electrician 12 years ago.
Can anyone help me determine why it took 3 to 4 days for this wiring to start a fire? And why it appears that the fire may have started at the circuit breaker panel, not at the dryer?
The fire had a tragic affect on my family. I am a master electrician. Thanks, TAH