No. I still would put more suspect on a weak connection in the panel, and may or may not even be part of the dyer circuit.But even that catastrophic failure did not ignite the house.
OP possibly recreating things that had no relevance to the incident, and apparently based on code issues observed with the dyer circuit, though he was told fire started at the panel.
Don't mean to be harsh and am sorry for his loss, but just think he is looking at wrong place for answers as to why the fire started. Fire starts because of heating where it shouldn't be, not because of a green insulated conductor being used for something other than code says it can be used for, or other similar things that involve theory more so than code.