From what was described, the only unusual condition on the panel side was that 10A was flowing on the EGC for the dryer circuit. Now that shouldn't cause a fire if all of the connections were good, but conceivably it might if there was a bad connection at some vulnerable location (assuming that one exists). However, before this dryer was wired up presumably there was negligible current in the EGCs, and so a bad EGC connection would have no effect (unless, of course, a significant ground fault occured). But after dryer was wired as described, 10A in the EGC might have exacerbated a lurking problem. Just speculation, but all I can do on this end.