Well, if we have anything to do with it, at 14.58A each tank requires a dedicated 20A circuit. For a 15A circuit 14.58 is well over 80%. Further, each cord should have a 5-20 plug.
I've long wondered how they get away with 5-15 plugs, and every manufacturer that makes equipment that scrapes by at slightly less than 15A puts a 15A plug on their equipment. I theorize that it's to make it less of a problem to use in existing kitchens that have 20A circuits with 15A receptacles. It will work- until you plug something else into the circuit. Then again that two tank fryer must be a real joy for some people when they plug both line cords into a duplex receptacle. :jawdrop:
I wonder how they get UL approval. I have found some equipment that says to use a dedicated 20A circuit for their 15A plug.
If you have a 5-20 plug it requires a 5-20 receptacle. It needs to be single and on a dedicated circuit because two of anything with a 5-20 plug is going to be more than 20A.
-Hal