One I can think of occurs whenever there are two groundings, either intentional (e.g., when a ground rod is provided for a generator) or when some other ground node exists that is part of the bonding in the house, with a higher ground impedance to the electrode underneath. These situations create a lower impedance path THROUGH the bonding between the nodes than through the earth.
When a lightning even occurs, a potential gradient is produced around the lightning strike. A house that is in this gradient, will experience the gradient...one side to the other....one ground node to the other. This voltage between ground nodes will result in current flowing up one node (GEC or the other ground point)...though the bonding EGC...and down the other node (other ground point or GEC). Equipment in the bonding path will be subject to whatever current/voltage exists due to the lightning strike and related impedance and couplings.
i believe you are looking at that wrong, please let me try to explain why i think that.
consider a copper wire, call it a #12AWG not that's its too relevant but to make sure we are on same page. say this #12 is feeding a light (100w incandescent if you want, but again not really relevant) , and the circuit is energized.120V
now say for what ever reason say we are in an electrician training lab and this wiring is all exposed and not buried in a wall or anything and its just single conductor thhn run on plywood
now say the "hot"(many call it that)(black wire)(neutral is white), now say the "hot" is stripped in two areas about 5' apart. now say you have rubber boots on whatever, say we are running this all off an isolation transformer with an ungrounded secondary. now i grab with one bare sweaty hand one of the bare spots in the black wire and the other bare spot with my other hand. i don't feel anything.
now if i would have a bare spot in the neutral wire and grab neutral with one hand and hot with the other i would get shocked.
now, how does this apply to what you were talking about
when i grabbed the black in two spots i was connected to the circuit in two spots. the thing is there was very little resistance between those two points in that black wire.
then when i switched it up i got shocked, not because white wires hate me, but because there was more resistance(the light) between the points i was grabbing.
so now i ask you, how is it that solidly bonding things creates more voltage gradients. you yourself just said a lightning stroke alone produces voltage gradients.
why do you think we use equipotential grounding grid in high voltage substations? the lower the resistance between everything the less the voltage will be between them.
if theres no resistance/impedance (me grabbing two parts in the black) there is a lot/almost no voltage/difference of potential, when there is resistance/impedance between the two parts (grabbing black and white) then there is a larger voltage/ difference of potential
now before you say i am short circuiting the circuit, i am, and thats what your bonding would do instead of something else(a person or flammable material) in the situation you referred to.