How does the neutral wire prevent MWBCs from operating at 240v?

Status
Not open for further replies.

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Roger's diagrams, Larry's written explanation, and the video Jamesco posted all do a good job of telling us what the neutral does but none explain why. How do the electrons on an unbalanced MWBC coming from phase A know they are supposed to turn right and head down the neutral path, and the electrons from phase B know they are supposed to turn left and head down the same neutral? Why don't they go wherever they want on whatever copper wire they like the best?

Tell me how this explanation works for you. Think of small beads. And the wire paths are 2" pipes. one pipe has a narrow part that is 1/2" in diameter, and the other has no restriction 2" all the way. With a 2" representing the neutral going back from the center. If you push beads in the end with 1/2" restriction, my common sense tells me that I will get an equal number of beads coming out of the "neutral" and the other "line" pipe. If I then, (for the other half of the cycle) push beads in the end that has 2" the whole way, my brain conceives that more beads will come out of the "neutral" than the 1/2" restricted other "line" In fact I am guessing about a 3 to 1 ratio.
 

kwired

Electron manager
Location
NE Nebraska
No. It works with DC, too. The direction of current in a DC version of a 3-wire circuit depends on which half of the circuit has more current.

Correct, put two batteries in series and connect two lamps from each end to mid point. If both lamps are same resistance the "neutral" current is zero. If lamps are different resistance - neutral will carry imbalanced current.

By connecting to the midpoint of the source you are assuring half the source voltage is what is applied to each load.

It is higher potential from end to end of the source so that is where the current is going to want to flow. If you have equal loads the "neutral" current theoretically is zero, realistically may be some very small current as the loads probably are not absolutely equal in resistance.
 

SG-1

Senior Member
See if this works for anybody

See if this works for anybody

The loads are in parallel with the phase & neutral.
We know that, in a parallel circuit the voltage across each load is the same voltage as the source it is in parallel with.

The voltage that is driving the current through the load is from the phase & neutral. The charge can only flow between those two conductors.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
The loads are in parallel with the phase & neutral.
We know that, in a parallel circuit the voltage across each load is the same voltage as the source it is in parallel with.

The voltage that is driving the current through the load is from the phase & neutral. The charge can only flow between those two conductors.

Um, no, not really. If two loads on different legs were perfectly balanced with no neutral current, then current flow in that moment would resemble a series circuit instead of a parallel circuit.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Um, no, not really. If two loads on different legs were perfectly balanced with no neutral current, then current flow in that moment would resemble a series circuit instead of a parallel circuit.

There would still be current on the neutral, they would just cancel out. If both ungrounded conductors were from the same phase, the neutral would carry twice the current, and if you lifted the neutral conductor nothing would work as there would be zero potential across the loads.

~~~~~~~~~~~~~~》~~~~~~~~~~~

If one were to wire up two 60 watt light bulbs, one on each leg of a multiwire branch circuit, and lifted the neutral, virtually nothing would happen to the lamps... If they had exactly the same resistance they would continue glowing at the same intensity. if one had a 120W and a 24 W bulbs wired on a multiwire branch , from a split phase source, they will see 120 volts each.. if you lifted the neutral in that configuration, the 24 watt bulb, having five times the resistance of the hundred 20 watt bulb, would see 200 volts to the 40 volts of the 120 watt bulb... It would glow brightly for a moment, burnout, open the now series circuit, and then the 120 watt bulb would no longer have a complete path and go out.

Edited to add... The reason why people burn up Electronics when they lose a service neutral is because most of them are lower wattage, higher resistance, therefore they have a higher voltage drop across them then something like a coffee pot, toaster, microwave, things that have a higher wattage
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You can think of it either way; as two groups of 120v loads in series supplied by a 240v source, sharing a neutral, or two separate groups of 120v loads supplied by two separate 120v sources, and those two independent circuits happen to share a conductor. The latter should be easier to understand, and you can simultaneously supply line-to-line 240v loads. That's your home service.

You could theoretically have two different 2-wire voltage systems, say one of 120v and one of 277v, share a neutral conductor, and the relative phase angle doesn't even matter. As long as only 120v loads receive their power from the 120v line conductor to the neutral, and only 277v loads receive their power from the 277v conductor to the neutral, they could share the neutral.
 

SG-1

Senior Member
Um, no, not really. If two loads on different legs were perfectly balanced with no neutral current, then current flow in that moment would resemble a series circuit instead of a parallel circuit.

Resembling & behaving that way is two different things. If the polarity were swapped on one of the transformer windings you would see the neutral current, because it would add in the neutral conductor.

If the loads are always perfectly balanced no neutral would be required. It's when people start throwing switches into the mix...:eek:hmy:

I can say a MWBC is two parallel circuits with a common return. It's the grounded conductor that forces the voltage across each load to be L-N, not L-L.
 

kwired

Electron manager
Location
NE Nebraska
There would still be current on the neutral, they would just cancel out.

I like that and it makes sense. On single phase three wire they are 180 degrees from each other and would cancel out.

On three phase with just two phases and a neutral they are 120 degrees from each other, neutral carries about same as the phase conductors when both have same load but add the third phase to the mix and they all cancel one another out on the neutral if balanced.
 

SG-1

Senior Member
Question: How does the neutral wire prevent MWBCs from operating at 240v?

Short Answer: By carrying the unbalanced load current.

I am going over to Jaggebens side.

A MWBC is a series parallel combination circuit.

Lets wire the neutral from the transformer center tap with a single wire for 2ft. then split it into two wires and go on to the loads.

For two perfectly balanced loads I can measure the neutral current along either wire until I reach the single conductor, then zip, zero, nada on my meter. MESH circuit analysis will show that the current in that portion is zero. ((Saying they cancel each other out is not exactly the same thing. This statement may be similar to "electricity always takes the path of least resistance")). The other explanation is that the current never entered the single conductor portion of the neutral conductor, but continued down to L2.

If the neutral is lifted with a balanced load, there is no effect on the operation of the loads. The current is supplied L1 to L2.
 

kwired

Electron manager
Location
NE Nebraska
Question: How does the neutral wire prevent MWBCs from operating at 240v?

Short Answer: By carrying the unbalanced load current.

I am going over to Jaggebens side.

A MWBC is a series parallel combination circuit.

Lets wire the neutral from the transformer center tap with a single wire for 2ft. then split it into two wires and go on to the loads.

For two perfectly balanced loads I can measure the neutral current along either wire until I reach the single conductor, then zip, zero, nada on my meter. MESH circuit analysis will show that the current in that portion is zero. ((Saying they cancel each other out is not exactly the same thing. This statement may be similar to "electricity always takes the path of least resistance")). The other explanation is that the current never entered the single conductor portion of the neutral conductor, but continued down to L2.

If the neutral is lifted with a balanced load, there is no effect on the operation of the loads. The current is supplied L1 to L2.

Which I think OP knows that, but asked why it works that way. I know it does what it does, but don't really know how to explain why.
 

SG-1

Senior Member
Question: How does the neutral wire prevent MWBCs from operating at 240v?

Short Answer: By carrying the unbalanced load current.

I am going over to Jaggebens side.

A MWBC is a series parallel combination circuit.

Lets wire the neutral from the transformer center tap with a single wire for 2ft. then split it into two wires and go on to the loads.

For two perfectly balanced loads I can measure the neutral current along either wire until I reach the single conductor, then zip, zero, nada on my meter. MESH circuit analysis will show that the current in that portion is zero. ((Saying they cancel each other out is not exactly the same thing. This statement may be similar to "electricity always takes the path of least resistance")). The other explanation is that the current never entered the single conductor portion of the neutral conductor, but continued down to L2.

If the neutral is lifted with a balanced load, there is no effect on the operation of the loads. The current is supplied L1 to L2.

No argument here.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
There would still be current on the neutral, they would just cancel out. ...

In the example I posted - perfectly balanced loads - they would cancel out to zero and no current would actually flow. It is admittedly a theoretical example, but what I said was correct.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Resembling & behaving that way is two different things. ...

In the example I posited there is no meaningful difference. Two balanced loads, lift the neutral, it behaves as a series circuit.

I can say a MWBC is two parallel circuits with a common return. It's the grounded conductor that forces the voltage across each load to be L-N, not L-L.

Your use of 'parallel' is contrary to the common definition, and does not help to explain how an MWBC works or why the voltage would be the same on both legs. In fact the voltage is not the same in the case of an MWBC; it is only nominally the same because the systems are designed that way by humans. The different phases of an MWBC are actually powered from different sources, and physics doesn't place any constraints on how different the voltages can be. The circuits happen to share a wire, which you can call a neutral or a common return, but they are not a parallel circuit. I could give you other examples of systems with common returns in which the voltages aren't even supposed to be nominally the same or polarities fixed. But in a true case of two paralleled circuits, physics dictates that voltage and polarity is actually and theoretically the exact same for both circuits on the side of the nodes where they are joined, because they actually go back to the same source.
 
Last edited:

SG-1

Senior Member
Still don't agree with your use of the term parallel. An MWBC doesn't share any important common feature with what we typically call parallel circuits.


One half of the transformer coil is wired in parallel with one of the loads. L1 to N. Voltage across the transformer coil is the same as the voltage across the load.
The second half of the transformer coil is wired in parallel with the other load N to L2. Voltage across the other transformer coil is the same as the voltage across the load.


It shares the most important common feature. The voltage across all components is the same.
 

SG-1

Senior Member
In the example I posited there is no meaningful difference. Two balanced loads, lift the neutral, it behaves as a series circuit.



Your use of 'parallel' is contrary to the common definition, and does not help to explain how an MWBC works or why the voltage would be the same on both legs. In fact the voltage is not the same in the case of an MWBC; it is only nominally the same because the systems are designed that way by humans. The different phases of an MWBC are actually powered from different sources, and physics doesn't place any constraints on how different the voltages can be. The circuits happen to share a wire, which you can call a neutral or a common return, but they are not a parallel circuit. I could give you other examples of systems with common returns in which the voltages aren't even supposed to be nominally the same or polarities fixed. But in a true case of two paralleled circuits, physics dictates that voltage and polarity is actually and theoretically the exact same for both circuits on the side of the nodes where they are joined, because they actually go back to the same source.

If one examines four receptacles that are wired in parallel & all have loads, then they are not really in parallel because of the voltage decreases at each receptacle ?
 