The debate seems to be whether a 120/240v supply is one 240v supply with a center tap or two 120v supplies that share a conductor.
I say the answer is that it's both, simultaneously. To a line-to-line load, it's the former; to a pair of line-to-neutral loads, it's the latter.
You guys are arguing over a distinction without a difference. It's both at the same time. I'm glad we're not arguing a 3-ph wye system.*
Did you guys read what I said in post #28? You could supply a 397v load line-to-line at the same time if the lines were at 180 degrees.
*Just to mention it now, it's the exact same thing, only with three lines and different timing. The timing is why the L-L voltage is lower.