Assuming (uh-oh!) you mean receptacle outlets, I use the "what's-the-load" method. Obvious are the single-receptacle circuits, like refrigerator, microwave, sump pump, central vacuum, etc. For kitchen counter receptacles, I like two or three.Beverly said::-? what method of electrical calculation do you use to figure out, how many outlets to put on a 15 & 20 amp circuit breaker ?
Lighting, no; receptacles, sometimes.stickboy1375 said:Larry you really wire bedrooms with #12 wire? IMO, I don't think I could justify that...
LarryFine said:Lighting, no; receptacles, sometimes.
In a typical 3-b/r, 1.5- or 2-bath house, one 15-amp lighting circuit for the bedroom/bath/hallway half and one for the kitchen/dining-room/living-room half. One 20-amp receptacle circuit supplies all of the bedroom and hallway receptacles, and a 15- or 20-amp circuit for the living-room and misc. (such as exterior and attic/crawl receptacles.)
When I lay out a bedroom, the lighting is #14 jumped from the smoke detector (which is necessarily already in the bedroom and normally very near or over the light switch). The receptacles are a 12-2 home run for each bedroom. As basements and panels in basements are standard fare in my area, the bedroom lighting home run will basically run from the panel to the basement smoke detector; often only 10 or 15 feet away.tallgirl said:When I lay out a bedroom, I take the home run to the light, 12/3 from the light to the switch, then exit the switch box out the bottom to the receptacles.
mdshunk said:When I lay out a bedroom, the lighting is #14 jumped from the smoke detector (which is necessarily already in the bedroom and normally very near or over the light switch). The receptacles are a 12-2 home run for each bedroom. As basements and panels in basements are standard fare in my area, the bedroom lighting home run will basically run from the panel to the basement smoke detector; often only 10 or 15 feet away.
Anything you want, unless there's a jurisdictional requirement or limitation. Seems a waste of a circuit to only have a few milliamps of load with just the smokes. Might as well use that circuit for bedroom lighting, I say to myself. It's already AFCI protected.tallgirl said:So ... what else can go on a circuit with a smokie?
Paul B said:We have strayed from the original post somewhat. On bedroom circuits I usually tryed not to have more then 8 recepts on a 15 and 11 on a 20 amp circuit. Someone stated 2 recepts on kitchen circuits, I've done some kitchen remodels that would have required 15 SA circuits if I did that. I never used to put recept and lighting on the same circuits, but with the AFCI I do now to save money.
Tallgirl why do you use 12 wire to the smokes?
Beverly said::-? what method of electrical calculation do you use to figure out, how many outlets to put on a 15 & 20 amp circuit breaker ?
roger said:Rocky, we need to note that in dwellings you can put as many as you want on a circuit, in other than dwellings it is limited to the 180 va per receptacle.
Roger
kingpb said:I would still use the 180VA per duplex receptacle, unless directed to do otherwise, and keep the lights separate from the recpetacle outlets. I understand that it is over the minimum required by NEC, but I am old school.
IMO, the Code is deficient in this area because of all the electronic gizmo's and what not's. It irriates me to no end to plug in an iron, and see the lights dim.