- Location
- Massachusetts
LarryFine said:If I'm correct, he's saying that he'd rather have the majority of the starting-current-induced voltage drop occur on the compressor's feed than the house's feeder. Reducing the compressor's supply size would reduce the voltage sag on the rest of the system.
Larry's nailed down what I was getting at.
But I do question this
Of course, the compressor will have a slightly shorter life
Why would you think that?
What does a soft start do?
It limits the current at start up just as 14 AWG would limit the inrush.
Keep in mind we are not delaying the motors wind up in seconds but in fractions of a seconds.
I think we could ague that limiting the start up current will make the motor last longer as long as the VD is not so great that the motor does not spin up in a reasonable amount of time.