They may not present a starting load, but you might want to hold them off until the across the line start motors are running.What is the point of delaying the motors that are on on VFDs?
More significant to me, in light of some of the questions and suggestions, is whether you want the delay from start signal to startup because you expect all of them to try to restart when the power come up after the transition? If so you might want to delay all of them from generator start rather than delaying the start signal of each one even if it happens long after the generator has started. But that will allow some other external event to cause all of them to try to start at once from generator power. Different fixed delays will not work if the start signals happen to be staggered wrong in time.
It really comes down to a need to prevent certain undesirable simultaneous start conditions when the generator is on, rather than imposing different fixed delays. Which suggests that the performance would be best when run by a small PLC.
The bad side effects of one simultaneous start bringing down the generator may well be costly enough to justify a PLC.