In most cases, we begin our calculations with the transformer, main breaker, and branch breaker.
However, when doing a solar project, we may estimate from the main breaker and inverter breaker for the combiner box by taping to the utility line.
How do you determine the precise value of Breaker KAIC without a transformer when the Inverter has provided the total OCPD per specifications?
The general electrical calculation for Electrical Panel.
First, we will calculate the full load current for the 1MVA transformer.
I F.L = P / (1.73 * V L-L ); where P is the transformer power rating in VA, and V L-L is the line to line RMS voltage at the secondary side of the transformer.
I F.L = 1,000,000/ 1.73*480 = 1,202 A; the I F.L is the full load current of the transformer. Now, to find the short circuit rating of point 1.
I S.C. for 3 Ph = I F.L /Z%; where I.S.C. is the short circuit current, and Z% is the transformer impedance; which usually can be obtained from the local utility company. I S.C. 3 ph for point 1 = 1202 /0.05 = 24,506 A or 24.5 KA (this is the available short circuit current at point 1)
F = (1.73 *50 *24,506) / (28,303*5*480) = 0.031206 ,
M = 1/(1+F) = 0.969738; where M is the multiplier, I S.C. 3 ph for point 2 = 24506* M = 24506*0.969738 = 23,764 A or 23.7 KA (this is the available short circuit current at point 2)
However, when doing a solar project, we may estimate from the main breaker and inverter breaker for the combiner box by taping to the utility line.
How do you determine the precise value of Breaker KAIC without a transformer when the Inverter has provided the total OCPD per specifications?
The general electrical calculation for Electrical Panel.
First, we will calculate the full load current for the 1MVA transformer.
I F.L = P / (1.73 * V L-L ); where P is the transformer power rating in VA, and V L-L is the line to line RMS voltage at the secondary side of the transformer.
I F.L = 1,000,000/ 1.73*480 = 1,202 A; the I F.L is the full load current of the transformer. Now, to find the short circuit rating of point 1.
I S.C. for 3 Ph = I F.L /Z%; where I.S.C. is the short circuit current, and Z% is the transformer impedance; which usually can be obtained from the local utility company. I S.C. 3 ph for point 1 = 1202 /0.05 = 24,506 A or 24.5 KA (this is the available short circuit current at point 1)
F = (1.73 *50 *24,506) / (28,303*5*480) = 0.031206 ,
M = 1/(1+F) = 0.969738; where M is the multiplier, I S.C. 3 ph for point 2 = 24506* M = 24506*0.969738 = 23,764 A or 23.7 KA (this is the available short circuit current at point 2)