Thank you kwired,
Happy Thanksgiving.
http://prntscr.com/97ogw6
I am still not understanding the primary current to use to size the OPCD and wires on the primary. According the screen shot I should be using another equation. I am just confused.
I didn't read all that kwired told you so uncertain what you do and don't understand...
There are two schema's for primary OCPD: 1) primary only transformer protection, and 2) primary and secondary transformer protection. Let's say for now that you are going to use the latter. Referring to Table 450.3(B) your primary OCPD is allowed to be rated up to 250% the primary rated current [typically; see Note 3]. Primary rated current at 15kVA 480V is 31.25A and 250% of that is 78.1A.... but you can't go up to next size, so max' std. OCP rating is 70A.
Keep in mind that you do not have to use that size. You can go smaller... but I would not go any smaller than the secondary OCP rating times the primary-to-secondary voltage ratio (and up to next std. size not over 70A). If you plan on using 60A secondary protection, that means I wouldn't go smaller than 35A on the primary.
Note for a 15kVA transformer, the secondary rated current is 62.5A and you can go up to 125% (78.125A) and go up from there to the next std. size (80A). So if you go this high, that would raise the smallest I would use for the primary to 45A.
Sometimes the deciding factor for primary OCPD is the primary conductor, which has to be protected per 240.4. If you go with a 70A OCPD for the primary, you essentially have to run 70A conductor.