electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
I would use the KW÷480×1.25. Which would be a 60 amp breaker with #6's. I'll be interested to see what someone else says. It's a good question. Not sure my answer is right........What is the correct way to size the branch circuit conductors and OCPD for this machine? Should I see what the HP of the motor is and look it up in the NEC tables and add 25%?
Yes. We still like our horsies here. The Europeans ate theirs...Thanks. I haven't looked at the actual motor, the thing is still crated up, but I assume the motor will be rated in kw, is that because it is European?
Sent from my SM-N920V using Tapatalk
I realize we should use the table for conductor sizwe but if the unit requires a 45 amp fla then I would use that and not 40 amps.
The overcurrent protective device usually, depending on a few factors, can be sized 250% of the fla. 430.52
Gardner Denver doesn't provide manuals on-line, you will need to call their local distributor most likely.
I'd base everything off the nameplate load of 45 amps. That should have power factor and efficiency built into it.
The 22kW might be motor output, might be compressor output.
Add: I guess it says motor capacity, but is likely output rating not input rating.
I figured that out after initial reply. But I bet that is rating of output shaft, once you figure out power factor and efficiency the rated input KVA is higher, and ultimately is the 45 amps @ 460 volts.the 22 kw is 'installed motor capacity'
Jraef brought up good points re: cooling and lube oil pumps. How would these small motors typically be protected? Internal fuses? I'd presume they are pretty small and even a dead short would fry either before tripping the unit's main breaker/fuses. Or would they be mechanically driven from the main motor?
That's something Ive never been clear on. When do I need to provide NEC overload protection for something that has a motor in it? Does the manufacturer take care of that? Am I supossed to dive into and dissect the whole thing and see if it supplied to meet the NEC? It would be nice if everything was supplied with the data like HVAC equipment, as Jraef mentioned. I often don't see that provided.