- Location
- Lockport, IL
- Occupation
- Retired Electrical Engineer
A colleague (a consulting engineer on a project that I am reviewing) and I have differing opinions regarding what to show on a panel schedule. We agree that the intent is to give the manufacturer sufficient information to be able to construct what is needed. We disagree on the method of conveying short circuit withstand ratings. I have been on a long (and mostly fruitless) campaign to get rid of all references to the term “AIC” on panel schedules. My reasoning (and my colleague is in agreement with this) is that panels do not interrupt current, so with regard to the panel itself the term is meaningless. I prefer to show “Short Circuit Current Ratings,” or SCCR, on the schedule, believing that is all the manufacturer needs in order to select the appropriate item from their product line.
My colleague is willing to add “SCCR” to the panel schedule. But he contends that an AIC value should be added as well, with a note that clarifies that the AIC pertains to the breakers installed in the panel. We both agree that a fault immediately downstream of a breaker would see a fault current equal to the “Short Circuit Current Available,” or SCCA, at the panel’s location. We agree that any breaker installed in the panel must have an AIC rating equal to or higher than the SCCA.
So the essential question I wish to present is this: how much is enough? Is showing an AIC rating sufficient to tell the manufacturer that all breakers must have at least that rating, AND THAT the panel itself must have at least that high an SCCR rating? Would showing just an SCCR value on the panel schedule be enough to convey the same message? Shall I drop my losing campaign and work instead on something more important, like convincing people to stop using “emergency generator” as a generic descriptor or using “amps per phase” just before adding the three phase amps to get total amps?
My colleague is willing to add “SCCR” to the panel schedule. But he contends that an AIC value should be added as well, with a note that clarifies that the AIC pertains to the breakers installed in the panel. We both agree that a fault immediately downstream of a breaker would see a fault current equal to the “Short Circuit Current Available,” or SCCA, at the panel’s location. We agree that any breaker installed in the panel must have an AIC rating equal to or higher than the SCCA.
So the essential question I wish to present is this: how much is enough? Is showing an AIC rating sufficient to tell the manufacturer that all breakers must have at least that rating, AND THAT the panel itself must have at least that high an SCCR rating? Would showing just an SCCR value on the panel schedule be enough to convey the same message? Shall I drop my losing campaign and work instead on something more important, like convincing people to stop using “emergency generator” as a generic descriptor or using “amps per phase” just before adding the three phase amps to get total amps?