- San Francisco Bay Area, CA, USA
- Electrical Engineer
As a specific case to discuss, the 2023 Code changes 210.8(A)(6) to eliminate the term "to serve the countertop surfaces" with regard to requiring GFCIs in kitchens. That means that ALL outlets in kitchens will need to be GFCI, including the one behind the refrigerator, which has been the last bastion of sanity in this regard (IMHO). So what I have already started seeing is that the appliance manufacturers are putting in statements such as "Do not install refrigerator on ground fault circuit", or words to that effect.
I believe this is an attempt from the appliance mfrs to give us "air cover" so that we can use a non-GFCI outlet, under the belief that 110.3(B) will trump 210.8(A)(6). But will it? I attended a local Code change seminar last year when 2023 was released, the general consensus among the presenters was that NO, 110.3(B) would not negate any other Code section. But most of the ECs in the room felt that AHJs would "look the other way" on this based on that issue. Of course I understand that from a construction standpoint, you could just install the GFCI, pass inspection, then tell the end customer to swap it out afterward, but that's not really the "right" way to address it.
Mind you, I'll be retired by the time 2023 goes into effect here in California, so this is strictly rhetorical at this point, but I'm very curious.