The hazard is the amount of Arc Flash Incident Energy (AFIE) typically expressed in cal/cm^2.The hazard does go down.
There is no industry consensus methodology, such as IEEE 1584, that calculates AFIE for anything except 3-phase (L-L-L) faults for 600V and less systems.
Yes, the first L-G fault on an HRG system is unlikely to result in a severe Arc Flash event. However, until the first fault is cleared, a second fault would be L-L which would likely propagate into a 3-phase event with the original AFIE level.
Reducing 'Risk' by lowering the probability of occurrence should be one of the goals of any Electrical Safe Work Practices program.
We need to use the definitions of the codes which which we are following.