My concern was actually on Nec 250.122 EGC for 15A breaker the EGC for CU is #14, so will it be ok to use #12 awg as the nec is the minimum and the EGC is not greater than the branch circuitWhy not (be comfortable) ?
#12 may not be necessary as in most case #14 would suffice. If voltage drop is a consideration, #12 might be appropriate but in an event it's no problem.