- Occupation
- Junior plan reviewer
I have RTU whose condensing unit has MCA of 30 amps and MOCP of 40 amps, 208V three phase. Can I use 240V, 30 amps disconnect current rating, three phase per code?
Likely yes. Keep in mind that MCA is 125% of compressor rated amps plus all other loads, therefore unit likely only draws maximum of 21-25 amps.I have RTU whose condensing unit has MCA of 30 amps and MOCP of 40 amps, 208V three phase. Can I use 240V, 30 amps disconnect current rating, three phase per code?
Sounds like the 240 volts is related to the rating of the disconnect.
240V is the disco voltage rating and 208V is service system voltage in which the disco is installed. Question is about hvac condensing unit nameplate mininum circuit amps (MCA) rating can be used as current rating of the hvac condensing unit disco.
Where in code it says this?I believe those non-fuseable disconnects should be => MAX FUSE rating per nameplate, not Minimum Circuit Ampacity.
Where in code it says this?
Sent from my SM-G935U using Tapatalk
It doesn't. It says the disconnecting means shall be at least 115 percent of the nameplate rated-load current or branch circuitselection current, whichever is greater.
Part II. Disconnecting Means
440.11 General. The provisions of Part II are intended to
require disconnecting means capable of disconnecting airconditioning
and refrigerating equipment, including motorcompressors
and controllers from the circuit conductors.
440.12 Rating and Interrupting Capacity.
(A) Hermetic Refrigerant Motor-Compressor. A disconnecting
means serving a hermetic refrigerant motor-compressor
shall be selected on the basis of the nameplate rated-load
current or branch-circuit selection current, whichever is
greater, and locked-rotor current, respectively, of the motorcompressor
as follows.
(1) Ampere Rating. The ampere rating shall be at least
115 percent of the nameplate rated-load current or branch circuit
selection current, whichever is greater.
Is "branch circuit selection current" the MCA?
How could the rated load current ever be greater than the branch circuit selection current?
No.
It can't be.
So what can be used to size current rating of HVAC disconnect then nameplate MCA or MOCP based on that code article nameplate rated load current or branch circuit selection current whichever greater?
See 440.2 for definition. It basically only applies if the overload protection allows it to run beyond the rated current.Is "branch circuit selection current" the MCA? How could the rated load current ever be greater than the branch circuit selection current?
Neither. You need the rated load current or branch circuit selection current to properly size the disconnect, though either the MCA or MOCP for a single compressor would be larger the required disconnect ampere rating.
Also, note that the quoted section 440.12(A) only applies to a single hermetic refrigerant motor compressor. 440.12(B) would apply to combination loads.
See definition in 440.2 - as worded BCSC should always be higher than rated load current.Ok so branch circuit selection current is it always higher than rated load current and MCA always higher than branch circuit selection current?
Sent from my SM-G935U using Tapatalk
Ok so branch circuit selection current is it always higher than rated load current and MCA always higher than branch circuit selection current?
IDK if they would use 125% of BCSC instead of rated current on units where this applies or not.
So MCA > BCSC > Rated load current. Whats the harm in using MCA as HVAC disconnect current rating?Yes and yes.
You still must be under HP rating of the disconnect with your equivalent HP - but likely will be in most cases, especially if using a "heavy duty" safety switch.So MCA > BCSC > Rated load current. Whats the harm in using MCA as HVAC disconnect current rating?