Genset Frequency vs ATS Sync Operation
Genset Frequency vs ATS Sync Operation
I am in agreement with the comments posted here with regard to smaller single phase gensets. But in a 3-phase commercial or industrial environment with larger units that are connected to automatic transfer switches the situation is quite different. These units typically employ in-phase monitors (sync check relays) that only allow load transfer when the phase angle of the two sources are within certain electrical degrees (usually < 10.) We like to see a difference of 0.2 Hz between sources to get a timely transfer in a hot bus-hot bus scenario. This occurs during retransfer back to normal after a power failure or a test performed from the test switch. Since utility frequencies are pretty much locked on to 60.00Hz, + or - 0.01 Hz, this would put the gen setting to 60.2 Hz. Greater than this value the sweep time becomes too fast (no transfer), less than this, sweep time is too slow and in some cases never reaches the sync window (timeout occurs) and locks out the ATS (mechanical failure fault.)
This condition applies only to 2 position, standard transition ATS units as opposed to 3 position, delayed transition units.