That a transformer? Lol I think I found the problem
I can't tell what it is from the picture. It might be a potted solid state control circuit.
In any case, even if you have not found the problem you have certainly found a problem.
Classic push on terminal problem, maybe the result of a wrong length wire in the harness? Or maybe just vibration?
 
Hz question

I'm thinking that's why its moved off the unit..... Wonder if an aftermarket avr would help this thing out a bit, at least those I can adjust


Sent from my iPhone using Tapatalk
 
Not that it is related to Hz, but I recently built a small panel with an analog ammeter and volt meter to monitor power usage when I am running on backup power. Since my genset is 30A 120V output, I used a 50A analog meter by Blue Sea Systems #9630. It came with the CT. As for the volt meter, it was also by blue sea #9353. I hooked it to a 15A CB. The gauges have a DC backlight so I added as 12V power supply to the monitor panel also served by the 15A CB. I have the 15A feed fused at 1A in the monitoring panel. The ammeter is only monitoring the genset feed so as soon as load is applied the gauge works automatically. I can check the volts and turn the backlight on by flipping the 15A cb on.
 
I've never seen one like this before
c120c3213dcf897f41c0b87804679287.jpg
.... That a transformer? Lol I think I found the problem


Sent from my iPhone using Tapatalk

This looks like a full wave bridge rectifier with 4 terminals: 2 AC input and 2 DC output. Could this be part of the DC field for the voltage regulator?
If so then a DMM with a diode scale can verify if it is defective and the culprit.
 
This looks like a full wave bridge rectifier with 4 terminals: 2 AC input and 2 DC output. Could this be part of the DC field for the voltage regulator?
If so then a DMM with a diode scale can verify if it is defective and the culprit.

Yep, @ATSman, you're right. I tried looking for that part # ZPQ 10 and saw it is ZPQ 10-50, a generator bridge rectifier.
 
Replacement Bridge Rectifier

Replacement Bridge Rectifier

You can Google bridge rectifier and find many substitutes for that one but this one rated
at 50A @ 1000V will surely work:

http://www.cnelectr.net/diodes/pdf/kbpc50005.pdf

also attached is a T-shoot guide for checking if a BR
is shorted or open circuited
 

Attachments

  • Bridge Rectifier KBPC5010W.pdf
    49 KB · Views: 0
  • RECTIFER_2E.bmp
    19.4 KB · Views: 0