RichB
- Tacoma, Wa
- Electrician/Electrical Inspector
OK-- base line stuff prior to the question--
I understand Voltage drop and the calculations, or thought I did until I was asked by a student, "What happened to using 10.7 for k?"
After really digging into it I haven't found a good answer, But what I have found is the following:
1. 12.9 seems to be for conductors at 90c
2. 10.7 seems to be for conductors at 65C
A. This is from a source I found on line--older--I think it was 50's or 60's--can't remember and can't find it again
3. I also realize that for AC we need to take Z into account--the reference I found said only for wires of #3 and above as it was negligible for wire sizes under that
4. Formulas I used
A. Vd=2(k)L(I) divided by CM
B. Vd=2(I)(Ohm/KFeet)(L/1000)
C. Where k-12.9 or 10.7
I=10
L=1000
CM=16510(#8)
Ohm/Kfeet=.778 (from Chap 9 table 8 for uncoated #8CU)
Here's the answers
15.63 Volt drop when k=12.9
12.96 when k=10.7
Using equation in B=15.56
It appears that using 12.9 is a quick way of finding Vd without knowing the ohms/Kft number-and gives a "Close enough working number"--does it also take into account the value for Z?
Since most of our (in my area and applications) conductors never reach 65C should we be using 10.7 or is 12.9 used like the second ground rod--do worst case and call it good?
I even found an old Simplex calculator on eBay and had to buy to see if I could find a date--BYW--It uses 10.7 according to the info printed on it I could read!!:ashamed:So at least I have a cool new circular calculator for my slide rule collection!!
I didn't post the calcs as this was getting long but if you want to see them I will
Thanks All!!!
4. Formulas I used
I=10
L=1000
CM=16510(#8)
Here's the answers
12.96 when k=10.7
Thanks All!!!