Sure... the 1" LB will suffice for bend radius requirement, but the conduit fill requirement will override the minimum LB size. According to Okonite, their 5/C 14AWG TC-ER has a 0.48" diameter. The minimum size GRC for it and one of the other two cables is 1-1/4"....
Both are 1" LB's and one shows #12 power wiring and the another one #10. Now, you have to look at these drawings that normally they also run a 5/c-#14 control cable in the same conduit and you can easily see that it is just would NOT be a good fit.
...