weressl
Esteemed Member
I think we're talking about two different things . What I'm thinking about is multiple breakers on a bus , with a " sum point " . Each phase current then goes to a bus relay , Example , an ABB type KAB . Maybe I got away from the original question . :smile:
I posted a transformer differential relay wiring, but a bus diferential relaying will work the same way.
GE Power Management publication GET8386.
CONCLUSION
External summation of the CTs may be considered under the following conditions:
1.
Neither of the two circuits that are paralleled is capable of producing any significant
fault current. Ideally they should feed pure loads.
2.
Even if the two circuits feed loads, some infeed is possible on ground faults through
the zero-sequence current unless the loads are connected in delta. The effect of the
zero-sequence infeed current on CT saturation must be considered when calculating
settings.
settings.
3.
The paralleled CTs are guaranteed to operate correctly (with minimal errors) in the
situation when there is not extra restraint and the fault current flows in and out of the
zone ?unnoticed?. Or, in other words, the pickup setting is high enough to prevent misoperation
due to saturation of the paralleled CTs.
4.
If needed, the situation shown in the above figure shall be identified through input
contacts, and appropriately settings shall be applied through multiple setting groups
in order to ensure security.
Overall, paralleling CTs for low impedance differential applications is always risky and shall be approached with maximum caution.
[FONT=Arial,Bold]
New York State Electric Meter Engineers? Committee Guide for Uniform Practices in Revenue Quality Metering
Rev. 4: August 20, 2003
3.8 CT secondary windings should not be connected in parallel.
There are schemes and special devices that do use multiple CT's for a single input, but it is not commonplace and their use is very selective and requires special care in selecting the CT's, matching their burden and having identical saturation curves.
[/FONT]