081205-1412 EST
weressl:
Relative to my post on the question of "total current" I was trying to find out from steve66 what he meant. Thus, if I put 3 Amprobe meters on the system, one on each hot conductor, use my eyes to read each of these meters, no interconnection of the meters, write down the values, and sum these three readings, then is this what he meant by "total current". I have no idea what "total current" means.
Yes, I am aware that in current transformer mode that putting the outputs in series produces no useful results. These are essentially current sources when loaded with a sufficiently low load resistance so that the core is not saturated.
The voltage at the input of the Siemens current inputs is always going to saturate at 20 MV and they also expect 10 MV at 5 A current as the nominal full scale. 20 MV will be saturation of the A/D converter. It also appears that resolution is either 1 part in 4096 or 2048 of the 20 MV value. There is always a fixed 0.002 ohm shunt resistor at each current input. The 10 MV input can be scaled to produce any desired display value within the adjustment range of the appropriate parameter. It appears they use a 16 bit word for storing this scale factor plus decimal point selection.
My point was that the current transducer probably has no chance of producing anything close to amperes into a 0.002 ohm load. And thus not much input voltage, and not much of a reading.
If these current transducers are actually what is connected to the Siemens instrument, then if there is known reasonable current thru one of the transducers, then a voltmeter measurement across the input terminals of Siemens should read near zero. If the transducer is disconnected from Siemens, then something between 0 and 1 V AC should appear across the transducer output. However, the transducer output leads should not be removed unless one is absolutely certain that this is a voltage output transducer vs a current transformer.
.