How about for feeder and service calculations?The MCA is the largest component (usually the compressor) *125% + the other loads. Curious as to why do you need to know the actual load?
How about for feeder and service calculations?
19.6 is the maximum load it is rated for. Conditions of operation will determine actual load, but should not exceed that. Not sure just how they came up with MCA of 31.9, unless there is other load not on the nameplate for some reason. It is usually 125% of largest load plus all other loads. Even taking both compressor figures x 1.25 still doesn't get us all that close to 31.9.I can clearly see MOPD is 40A for this 460V 3 phase compressor.
Next I see Minimum Circuit Ampacity is 31.9A
Two or more people told me that this is the load. I disagree.
The load is Fan Motor FLA(1.0*2) + Compressor Motor RLA (7.3+10.3) =19.6A
Who is correct???? View attachment 20729
Elaborate on why you believe 31.9A is the running load. It cannot be that since it would heat up the wire.The math is already factored in there use a 40a breaker or fuse with conductors suitable for 31.9 amps
Sent from my SM-G950U using Tapatalk
kwired, I agree, that MCA is a puzzlement.
I wonder if this a VRF system with multiple evaporator units. Note the label says the electrical characteristics are for the outdoor unit only. That might explain the discrepancy.
FWIW, I usually find the actual load to be about 66% of MCA. I am not saying there are not exceptions, but most I have measured have been right about there.
These VRF units usually draw less than that but manufacturers are required to calculate worst case.
I should also note in my previous post I should have said RLA is just a percentage of compressor overload values.
Load on a compressor is effected by how much heat is being moved by the refrigerant, and conditions of the heat exchanger coils can have an impact. Plugged condenser coil can't get rid of heat - leaving the system running at higher pressure and loading the compressor even more then usual.FWIW, I usually find the actual load to be about 66% of MCA. I am not saying there are not exceptions, but most I have measured have been right about there.
VRF needs to be running at 100% before it will reach RLA. When you first start system up you might get 100% speed but still depends on actual refrigerant loading as to what the motors will draw. In heating mode you may see 100% speed more often then during cooling mode - but there isn't as much heat being moved during extreme cold conditions and it won't be as much load on the system.These VRF units usually draw less than that but manufacturers are required to calculate worst case.
I should also note in my previous post I should have said RLA is just a percentage of compressor overload values.
So, is #10cu adequate, or must #8cu be used?MCA = 1.25X23.9 + 2 = 31.9!
Unless you must use 60C ampacity table, 10AWG is good.So, is #10cu adequate, or must #8cu be used?
How about for feeder and service calculations?