JasonCo
Senior Member
- Location
- Houston, Texas
I have a homework question that reads:
A 240v, 3-ph, 3-wire panel is fed from a 100 KVA 3phase transformer that has Z = 1.8% on its nameplate. The transformer is supplied power from a 3-pole breaker in a 277/480v, 3-ph, 4-wire panel. If the Aphase and the Bphase feeder conductors going to the 240-volt panel are "shorted" together inside the transformer enclosure, about ___ amps of current will flow through the transformer winding.
A. 23,148
B. 7,716
C. 6,682
D. 13,365
E. 11,574
Okay so Equation is I = VA / (E x 1.732 x Z)?
So I do 100,000 / (480 x 1.732 x .018) = 6,682
My question is though, that the "shorted" part of the question is throwing me off, its talking about Aphase and Bphase shorting together, sending ___ amps down the transformer windings? So I see that answer choice D is double answer choice C. 6,682 x 2 = 13,365.
Do I have to multiply it by 2, just unsure what to do when the question throws in this "shorted" part...
A 240v, 3-ph, 3-wire panel is fed from a 100 KVA 3phase transformer that has Z = 1.8% on its nameplate. The transformer is supplied power from a 3-pole breaker in a 277/480v, 3-ph, 4-wire panel. If the Aphase and the Bphase feeder conductors going to the 240-volt panel are "shorted" together inside the transformer enclosure, about ___ amps of current will flow through the transformer winding.
A. 23,148
B. 7,716
C. 6,682
D. 13,365
E. 11,574
Okay so Equation is I = VA / (E x 1.732 x Z)?
So I do 100,000 / (480 x 1.732 x .018) = 6,682
My question is though, that the "shorted" part of the question is throwing me off, its talking about Aphase and Bphase shorting together, sending ___ amps down the transformer windings? So I see that answer choice D is double answer choice C. 6,682 x 2 = 13,365.
Do I have to multiply it by 2, just unsure what to do when the question throws in this "shorted" part...