Does anyone know of a quick method for identifying neutral wires in a panel. I am splicing circuits in a main panel and taking them to a subpanel and they are not readily apparent. Any suggestions will help my task, thanks.
That could be dangerous if he isn't sure where the neutral is going (or if 1 or 2 more hots are using it).Theoretical answer: get a 200W bulb and a flasher. Hook it at the load end. Use an ammeter and search for varying amps in the neutrals.
Once identified, wirenut the hot and neutral in the panel, check the resistance at the load end of the circuit.
Good Luck!
That could be dangerous if he isn't sure where the neutral is going (or if 1 or 2 more hots are using it).
That's something that I have always done. I also label boxes with the panel and circuit number.It is indeed a problem. I'm had a change to 2014 NEC accepted so far that would require the identification of the neutral, hot pairings during installation.
That could be dangerous if he isn't sure where the neutral is going (or if 1 or 2 more hots are using it).
I don't see how that will determine which circuit(s) a neutral serves on a grounded neutral system. All neutrals should "ping" to ground regardless of test points.turn off all loads, use your volt meter set it on continuity and go each wire to ground the neutral should beep.
If every circuit has it's own neutral, then you can use an amprobe to find which neutral goes with each hot.
Just measure a hot that you want to move, see what it reads. Now measure the neutrals and find one with the same reading/ When you find one that you think may be it, turn off the breaker to that hot and see if the current on the neutral goes to 0, this will confirm it for you.
True, but in my experience live tracers are not as effective in finding the neutral conductor, compared to finding the associated circuit breaker, because at the panelboard all the neutral conductors are more solidly connected together and commonly routed in near proximity to each other. Ceating separation between neutral conductors will help, as will physically narrowing down possible mating with ungrounded conductors. The tracer should have a means of signal strength indication. If using this method, I suggest using it in combination with another verification method which does not include disconnecting the neutral conductor while ungrounded conductors are energized. ?JMO?If you are trying to pair up neutral conductors with their respective ungrounded conductors use a simple breaker finder tracer on live lines. Both circuit conductors will have signal. ...
True, but in my experience live tracers are not as effective in finding the neutral conductor, compared to finding the associated circuit breaker, because at the panelboard all the neutral conductors are more solidly connected together and commonly routed in near proximity to each other. Ceating separation between neutral conductors will help, as will physically narrowing down possible mating with ungrounded conductors. The tracer should have a means of signal strength indication. If using this method, I suggest using it in combination with another verification method which does not include disconnecting the neutral conductor while ungrounded conductors are energized. ?JMO?