Re: Igniter for Instant HW heater
Originally posted by sfav8r:
If I have an appliance that allows a cord, but is fastened in place more securely than allowed for in 422.16, which do we comply with?
Here is the installation instructions for the TK-D20 you
posted.
Electrical Connections
The T-KD20 requires a 60 Hz 120 VAC electrical
power supply, and it should be properly grounded
in accordance with the most recent edition of the
National Electrical Code, ANSI/NFPA 70 and any
local codes. In Canada, all electrical wiring to the
heater should be installed in accordance with the
Canadian Electrical Code, CSA C22.1 Part 1, and
any local codes. Do not rely on the gas or water
piping to ground the metal parts of the heater.
CAUTION: Label all wires prior to disconnection
when servicing controls. Wiring error can cause
improper and dangerous operation. Verify proper
operation after servicing.
? A means for switching off the 120 VAC power
supply must be provided.
? Wire the heater exactly as shown in the wiring
diagram.
? A green screw is provided in the junction box
for the grounding connection.
I can?t see anywhere that it allows it to be cord and plug connected. However I do see where it requires a switch to be installed for a disconnecting means.