kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
As I was reading through posts I kept thinking of voltage monitoring equipment and shutting down either by dropping contactors or shunt trip mains etc. then I saw your isolation transformer - probably the best idea. 240 volts in 120/240 out it won't care if there is an good neutral or not on the supply side. If you lose an incoming grounded conductor you will have no primary current and therefore no secondary voltage. They are a little expensive if you need to go over 15-25 kVA but if he has battled this for as long as he says - it probably doesn't look all that expensive compared to what has needed repaired/replaced in the past.I didn't think about the response time. I guess you would have to trip in 0.06 cycles to be inside the CBEMA curve for 200% voltage. Perhaps in conjunction with UPS and/or surge protector would help dampen the overvoltage for long enough. I'll leave that up to someone else to look up.
Perhaps an isolation transformer is the way to go.
How about some preventative maintenance. Sounds like the equipment you require is a chainsaw.....cutting down the trees in the easement might help decrease the chances of this happening again.
Or have the POCO secondary put underground then you won't have to worry about trees anymore. Tree trimming gets forgotten about - until the next downed line incident, and they grow back faster then one realizes many times.