Here is my scenario, a customer wants to put an RV hook-up on the property. It is a 30A RV and they want it to have it's own service. There are three mobile homes in line adjacent to the site for the RV.
POCO says they can't run the secondaries any further then they already are because the three mobile homes are all on the same transformer. To run new primaries and set another transformer is cost prohibitive. POCO says they will allow another service at the last mobile home, on/adjacent to the existing pole. This is with stipulations that I won't get into for now.
From the last mobile home it is 108' to where the RV box needs to be. That's not counting the distance from the meter to ground nor ground up to RV box. So lets just say 123'. I know the NEC doesn't require adjusting for voltage drop. But I was talking with the inspector and he suggested running #6 wire due to the fact that the secondaries are already maxed out and adding another 100+ feet might cause problems.
Now normally 30A only needs #10 AWG wire, do you think I would need to go all the way to a #6 for this? I was thinking #8 would do it. AFAIK, the RV would only have one A/C unit, receptacles and lights. Normally the stove would be gas and sometimes the fridge. I'm not sure exactly what the load would be, but it can't be over 30A. In case some don't know, the 30A is single pole, single phase, not 2-pole 30A.
Thoughts?
POCO says they can't run the secondaries any further then they already are because the three mobile homes are all on the same transformer. To run new primaries and set another transformer is cost prohibitive. POCO says they will allow another service at the last mobile home, on/adjacent to the existing pole. This is with stipulations that I won't get into for now.
From the last mobile home it is 108' to where the RV box needs to be. That's not counting the distance from the meter to ground nor ground up to RV box. So lets just say 123'. I know the NEC doesn't require adjusting for voltage drop. But I was talking with the inspector and he suggested running #6 wire due to the fact that the secondaries are already maxed out and adding another 100+ feet might cause problems.
Now normally 30A only needs #10 AWG wire, do you think I would need to go all the way to a #6 for this? I was thinking #8 would do it. AFAIK, the RV would only have one A/C unit, receptacles and lights. Normally the stove would be gas and sometimes the fridge. I'm not sure exactly what the load would be, but it can't be over 30A. In case some don't know, the 30A is single pole, single phase, not 2-pole 30A.
Thoughts?