mstrlucky74
- NJ
Guys is it possible with an Ilsco or Polaris type tap block to go from 6 sets to 8 sets as shown? Thanks.
Ron: Would the 14 port still not work... only requiring alternating incoming and outgoing.https://commerce.ilsco.com/e2wShopp...k=2100001183:3100012208:3100012512:3100012872
They have them up to 14 ports, so it seems possible to have 6 incoming and 8 outgoing in the same tap connector
Edited, actually, maybe not " For multiple inputs, the inputs must be staggered with outputs to allow for ampacities to be additive per NEC Table 310.16 and 310.17"
Alternating incoming and outgoing would only permit 6 in, 7 out at best.Ron: Would the 14 port still not work... only requiring alternating incoming and outgoing.
How would the 14 port work if I have 28 conductor coming in(actually what about the grounds??) that would make it 5x6 sets...30 conductors getting tapped to the 8 sets.
How about using (2) 7 port connectors for each phase?
Cheers, Wayne
No, they must all land on the same termination or we are into violations.
So, (2011) 310.10(H)(2)(5) says that parallel conductors must "Be terminated in the same manner." I'm just trying to figure out what that means. Certainly if they all are terminated on the same connector that fits the bill. But does the language require them to be terminated on the same connector?
Physics-wise, any properly symmetric arrangement will work, and so the question is whether that would be considered to be terminated in the same manner. The simplest case would be converting from 2 parallel sets to 4 parallel sets, with each conductor of the parallel set of 2 connected to 2 conductors of the parallel set of 4.
Cheers, Wayne
It's a matter of overcurrent protection, if all the conductors do not terminate together you are no longer in pararallel. I am not explaining this well but it is the deal.