Originally posted by kendog:
you're still missing the part of the exception thats says receptacle outlet and not receptacle. the main rule also says receptacle outlet and not receptacle. what if you put a gas range on a 15 amp breaker with a duplex recpetacle. Your saying that since the range only use on recpetacle of the duplex the other receptacle would be in violation even though no one in there right minde is going to pull the range out to use the extra receptacle. When there is a perfectly good one with in 2' of the range.
No I am not missing anything in either exception.
Yes I am saying that a receptacle that is installed for any of the following must supply current for that piece of equipment ONLY!
210.52(B)(1) exception (1) to replace the required lighting outlet and it MUST be switched and on a general lighting circuit
210.52(B)(1) exception (2) an outlet on an individual circuit can contain one receptacle for each piece of refrigeration equipment
I am also saying that the exception to which you have referred to are to be on the small appliance circuit as outlined in their section
210.52(C) exception (1) allows a clock to be installed on a small appliance circuit
210.52(C) exception (2) allows the light and igniters for a gas range to be installed on the small appliance circuit.
Any receptacle (singular) that is installed other than those that are in use as outlined by the above mentioned exceptions are REQUIRED to be on a 20 amp circuit no matter if it is behind anything or not.
Circuits and receptacles that are installed to supply dishwashers, disposals and hood fans are outlined in 422.
Circuits and receptacles installed to supply ranges are outlined in 210.19 and 220,55