If it is not above the countertop, it is not serving the countertop. The kitchen GFCI rule only applies to receptacles that serve countertops.Because then it will be serving as a small appliance or in realistic perposes, a countertop .
I agree that there is a difference between "dedicated branch circuit" and "individual branch circuit." The difference is that the second is defined by the NEC, and the first is trade slang. But it is not true that bathroom receptacles are to be on a dedicated circuit. The exception to 210.11(C)(3) gives us another option.Originally posted by throttlebody: Jim, the bathroom receptacles are to be on a dedicated circuit. . . . From interpretation, there is a difference between dedicated and individual branch circuits.
If a circuit is run to a bath to serve just the required receptacle providing that we are speaking about a single point in which power is utilized then a standard gfci is fine.They are rated as 20 amps and if not mistaken aren`t they rated as 15 amp feed through ???Originally posted by throttlebody:
Why? It is not serving the kitchen countertop. If it is on the far wall of the kitchen, mounted about 18" AFF, serving as a wall receptacle, you would still require GFCI protection? What about the ones inside of the cabinets for the microwave, disposal, dishwasher, ect. Those are accessible.Originally posted by RUWired:
I have to add my two cents worth also in the discussion.If this duplex receptacle becomes accessible because of any reason, then it must become a GFI receptacle.
Rick
Jim, the bathroom receptacles are to be on a dedicated circuit. They don't need single receptacles installed. From interpretation, there is a difference between dedicated and individual branch circuits.
Is there any difference between "dedicated branch circuit" and "individual branch circuit."?Originally posted by charlie b:
I agree that there is a difference between "dedicated branch circuit" and "individual branch circuit." The difference is that the second is defined by the NEC, and the first is trade slang. But it is not true that bathroom receptacles are to be on a dedicated circuit. The exception to 210.11(C)(3) gives us another option.Originally posted by throttlebody: Jim, the bathroom receptacles are to be on a dedicated circuit. . . . From interpretation, there is a difference between dedicated and individual branch circuits.
Some times the two of us disagree about things found in the NEC and I think that this is healthy to our mental state.Originally posted by Charlie B
This has been an exercise in reading the words, as those words are written. The only thing clear to me, from this discussion, is that the various authors of the various NEC sections were not consistent, in the way they chose the words.
Although the word ?dedicated? is not found in article 100 of the NEC the NEC does use the word when referring to a circuit as outlined in 210.8(A) exceptions 2, 3, 5 and the exception to 210.8(B) 4Originally posted by Charlie B
I agree that there is a difference between "dedicated branch circuit" and "individual branch circuit." The difference is that the second is defined by the NEC, and the first is trade slang.
You are abosulutely right. How forgetful of me to not include the exception. I apologize for not being more thorough in my intent to point out the differences. I shall include it now in a question.Originally posted by charlie b:
I agree that there is a difference between "dedicated branch circuit" and "individual branch circuit." The difference is that the second is defined by the NEC, and the first is trade slang. But it is not true that bathroom receptacles are to be on a dedicated circuit. The exception to 210.11(C)(3) gives us another option.
That is funny!Originally posted by jwelectric:
I have a hard time thinking that these people would use a slang term in a legal document though.
My money lies that most will pick I onlyWhich of the following best describes a transformer as outlined in 450.2.
I- A woman and here make up early in the morning.
II- A kids toy
(a) I only (b) II only (c) Both I and II (d) Neither I nor II