Anwar Pasha
Does NEC code allow to install more than one water heater on the same circuit? Where can I find about it in NEC!
I know that generally they are not permitted, but is their any NEC code pertaining it!
210.23(A)(1) Cord-and-Plug-Connected Equipment Not Fastened in Place. The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
These are normal domestic water heaters (portable ones) of 1200 watts, 220v single phase. I know that generally they are not permitted, but is their any NEC code pertaining it!
I am sorry for misscommunication, its a storage type water heater. I went through article 422 but still the doubt whether two or more storage water heater can be feeded from a single circuit.
422.10(B) Circuits Supplying Two or More Loads. For branch circuits supplying appliance and other loads, the rating shall be determined in accordance with 210.23.
210.23 Permissible Loads.
In no case shall the load exceed the branch-circuit ampere rating. An individual branch circuit shall be permitted to supply any load for which it is rated. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.
(A) 15- and 20-Ampere Branch Circuits. A 15- or 20-ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2).
Exception: The small-appliance branch circuits, laundry branch circuits, and bathroom branch circuits required in a dwelling unit(s) by 210.11(C)(1), (C)(2), and (C)(3) shall supply only the receptacle outlets specified in that section.
(2) Utilization Equipment Fastened in Place. The total rating of utilization equipment fastened in place, other than luminaires, shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.
That is for a single appliance so how does that apply?In all probability 422.11(E) is going to prevent such an install.
It applies to each appliance, you cannot decide to run a 100 amp circuit to supply ten - 9 amp appliances.
Now how does that apply to each one. The branch circuit supplies more than a single appliance.
I never said you could run a 100 amp circuit either.