jumper
Senior Member
- Location
- 3 Hr 2 Min from Winged Horses
Again, I've no need to find out. I'm not saying that to be rude, just admitting that I'm not an expert at that part of the Code because I already know that every 120V machine I've ever seen (up to 5-tons, with a 3/4 HP blower) is already on a dedicated 15A breaker, #14 wire, and either a NEMA 5-15 receptacle or 15A switch. I work on these machines for a living, and see different ones every day, residential and commercial.
.
Question: I thought at the beginning this was just an air handler like the inside unit of a heat pump, but it is a gas furnace instead. I am guessing the AC coil in part of this unit, not that matters here.
Would not there be a nameplate on the unit with MCA and MOCP given?
As you mentioned for disconnecting means:
If these units are cord connected, the receptacle works.
If hard wired, a switch is prolly used, although I have gotten leery of using snap switches in many cases.
The HP ratings are a lot lower than one expects. I like the el cheapo pull out discos for less than $10. 60A and 10HP rating, I know it works.