Some like cord and plug since its cheap, but, can you use your every day cord whip on a 25 amp rated outlet like the OP is up against?
I think not...
Well that is a bad idea.But manufacuter calls for mocp 15 amps. Engineer is runing #10 awg from 25 amp circuit breaker to 20 amps motor control switch. The switch load side is connect to fans.
Sent from my SM-G935U using Tapatalk
And a code violation to boot!Well that is a bad idea.
I like to see the plug sitting in front of me while I'm working on a machine, especially when diagnostics will have you connecting and disconnecting several times. Same reason I prefer a pull-out instead of a switch-type disconnect at the unit outside.
And a code violation to boot!
The MOCP is not a recommendation; it is a listing requirement enforceable by the NEC.
Sent from my XT1585 using Tapatalk
I don't see this as a code violation. The Goodman manual calls the MOCP the maximum "RECOMMENDED" fuse or circuit breaker size.
It further states to size wires and fuses properly in accordance with the NEC. It doesn't appear to be a listing requirement to me.
And why would you want to take responsibility for oversizing the overcurrent projection recommended by the manufacturer?
To me, if you do, you've just voided all warranties should problems arise by doing so.
JAP>
How would you void a warranty be installing the unit per both Code and the manufacturer's instructions?
Putting a 25 amp rated overcurrent device ahead of something that recommends 15 doesn't seem to me to be installing the unit per the instructions.
JAP>
They don't instruct you to use a 15A OCPD, they recommend that you do.
They instruct you to size the wire and fuses in accordance with the NEC and/or any local codes.
They don't instruct you to use a 15A OCPD, they recommend that you do.
They instruct you to size the wire and fuses in accordance with the NEC and/or any local codes.
Off topic a little but a good example - what is purpose of requiring semiconductor fuses in the supply circuit of VFD's besides complying with instructions?CYA is all that is.
To me although maybe not a code violation by doing otherwise, you're always better off to follow the Manufacturers recommendation.
If the wiring in the unit were to fry for some unknown reason and cause damage , I'd have a stiffer leg to stand on if the investigator found it was protected by the recommended OCPD rather than 10 amps above the recommendation , where I wouldn't stand a chance.
JAP>
Off topic a little but a good example - what is purpose of requiring semiconductor fuses in the supply circuit of VFD's besides complying with instructions?
In such application if motor is drawing too much current drive protects itself and shuts down. If a front end component of the drive shorts out - it is toast whether you had a semiconductor fuse installed or not. Some fuses may reduce how spectacular that failure may be, but is still toast.
Do soft start prevent voltage drop due to voltage drop from long distance cable run?
Off topic a little but a good example - what is purpose of requiring semiconductor fuses in the supply circuit of VFD's besides complying with instructions?
In such application if motor is drawing too much current drive protects itself and shuts down. If a front end component of the drive shorts out - it is toast whether you had a semiconductor fuse installed or not. Some fuses may reduce how spectacular that failure may be, but is still toast.
Your right, that is way off topic.
More like riiiiinnnnggggg... hello....I need you to get over here...fire marshall is here and found the cause of what burnt my house down is the wiring inside my furnace you just wired for me the other day....me ... sorry ... that's not my problem... I wired it per code......that maybe but we already called the furnace manufacturer and they aren't taking responsibility for the fire....we told them yes they were because the fire started in the faulty wiring in the unit they sold us and we were going to sue their pants off.....they then asked us what size OCPD the installing electrician put in and the fire Marshall found that you put in a 25 amp breaker instead of the 15 amp they recommended so now they're blaming you because you put in a breaker larger than what they recommended...and I'm now going to sue your pants off...me... click...dddduuuuuhhhhhhhhhhhhhh....
One can replace furnace in your little story with VFD and 25 amp breaker with semiconductor fuse and leave the rest of the wording as is and you are telling almost same story just with different equipment involved.Your right, that is way off topic.
More like riiiiinnnnggggg... hello....I need you to get over here...fire marshall is here and found the cause of what burnt my house down is the wiring inside my furnace you just wired for me the other day....me ... sorry ... that's not my problem... I wired it per code......that maybe but we already called the furnace manufacturer and they aren't taking responsibility for the fire....we told them yes they were because the fire started in the faulty wiring in the unit they sold us and we were going to sue their pants off.....they then asked us what size OCPD the installing electrician put in and the fire Marshall found that you put in a 25 amp breaker instead of the 15 amp they recommended so now they're blaming you because you put in a breaker larger than what they recommended...and I'm now going to sue your pants off...me... click...dddduuuuuhhhhhhhhhhhhhh....
Not sure if you are absolutely serious or joking?Do soft start prevent voltage drop due to voltage drop from long distance cable run?
Sent from my SM-G935U using Tapatalk