I not going to answer your question because of the forum rules. However, I will make some additional comments.
First, most electricians do not have a good understanding of basic electrical circuit theory, and therefore, don't think of many different solutions. Thus, they may not be real useful in solving your problem.
I ran an experiment with a 30 ft cable, applied 120 V to a lead, and measured the capacitively coupled voltage to another wire in the cable. With just a Fluke 27 as the load ( 10 meg input resistance ) I read 0.29 V ( 29 millivolts ). Shunt loading with 15 k ohms across the meter input the reading dropped to 0.003 V ( 3 millivolts ). 15 k is in the ballpark of a typical 120 V solid-state input.
Your problem can be solved with the correct help.
.