I was inspecting a pool in ground and found some problems I thought?
1-several neutrals under 1 termination. 408.21 you are only permitted 1
2-the deck box which is about 10' from pool and approx. 12" off ground. I had asked to provide an approved seal according to 680.24(B)(1)(3).
3-The feed for the pump motor went from the house to a timer 240V than to the pump hard wired. the timer was rated for motor and had a lockable cover and on/off lever. could this be used as motor disconnect?
Also I asked for a disconnecting means for the motor controller.
680 doesn't address motor controllers. went to 430.81(A) which describes motor controller. it fits . so went to 430.102(A) which calls for a disconnecting means for the motor controller? Please I am looking for feed back.