Pay day is friday , s--- runs down hillWhat other rules have I been missing out on?
Pay day is friday , s--- runs down hillWhat other rules have I been missing out on?
The thing that I don't understand is, what section of the NEC mandates that the customer's equipment be listed?
What other rules have I been missing out on?
In the 2005 NEC, the word listed, is mentioned 1116 times. Depending on the equipment being referenced in the NEC, there may be no need for listed equipment.
In NYS, the state code books require that all equipment being installed is to be listed. I do not know how that is even possible, but that is what is written.
Please tell me you didn't spend a weekend counting how many times
the word "Listed" appears in the NEC. :grin:
90.7 Examination of Equipment for Safety.
For specific items of equipment and materials referred to in this Code, examinations for safety made under standard conditions provide a basis for approval where the record is made generally available through promulgation by organizations properly equipped and qualified for experimental testing, inspections of the run of goods at factories, and service-value determination through field inspections. This avoids the necessity for repetition of examinations by different examiners, frequently with inadequate facilities for such work, and the confusion that would result from conflicting reports on the suitability of devices and materials examined for a given purpose.
#1. "Almost done" is not the same as "done".
#2. If you needed a ladder to install it, I probably need a ladder to inspect it.
#3. Saying you don't have tools with you doesn't mean it won't get opened, it just means I'll have to walk out to my truck and get my tools and we'll be opening a lot more.
#4. "I ran out of ______," is not a good excuse.
#5. I never get to say, "I'm to busy to do your inspection", so you shouldn't be to busy to be there (depending on the inspection).
#6. I know, we're the only ones calling that. (See #4).
#7. I love a good argument, let's just make sure that we both have something to back it up with. (Paper work, code book, etc.)
#8. No matter how far over my head you go, I am the only person in our city with my experiance, and I will eventualy be asked my opinion or side. I can always back it up. (See #7)
#9. A phone call can save a lot of headache later. If I don't know the answer, I will find the answer as quickly as I can for you.
Before anyone jumps all over me, I added the smiley faces so you would all know that this is all in fun.![]()
In the 2005 NEC, the word listed, is mentioned 1116 times. Depending on the equipment being referenced in the NEC, there may be no need for listed equipment.
In NYS, the state code books require that all equipment being installed is to be listed. I do not know how that is even possible, but that is what is written.
If rule #1 can be bent just a little bit I will happily accept all the rest.#1. "Almost done" is not the same as "done".
#2. If you needed a ladder to install it, I probably need a ladder to inspect it.
#3. Saying you don't have tools with you doesn't mean it won't get opened, it just means I'll have to walk out to my truck and get my tools and we'll be opening a lot more.
#4. "I ran out of ______," is not a good excuse.
#5. I never get to say, "I'm to busy to do your inspection", so you shouldn't be to busy to be there (depending on the inspection).
#6. I know, we're the only ones calling that. (See #4).
#7. I love a good argument, let's just make sure that we both have something to back it up with. (Paper work, code book, etc.)
#8. No matter how far over my head you go, I am the only person in our city with my experiance, and I will eventualy be asked my opinion or side. I can always back it up. (See #7)
#9. A phone call can save a lot of headache later. If I don't know the answer, I will find the answer as quickly as I can for you.
Before anyone jumps all over me, I added the smiley faces so you would all know that this is all in fun.![]()
The thing that I don't understand is, what section of the NEC mandates that the customer's equipment be listed?
I'm curious about this, as well...
I don't see anything in that section that requires listing. I see a couple sentences devoted to telling the industry at large that listing speeds the inspection process.90.7 Examination of Equipment for Safety.
For specific items of equipment and materials referred to in this Code, examinations for safety made under standard conditions provide a basis for approval where the record is made generally available through promulgation by organizations properly equipped and qualified for experimental testing, inspections of the run of goods at factories, and service-value determination through field inspections. This avoids the necessity for repetition of examinations by different examiners, frequently with inadequate facilities for such work, and the confusion that would result from conflicting reports on the suitability of devices and materials examined for a given purpose.
If rule #1 can be bent just a little bit I will happily accept all the rest.
I would demand the inspector show me a code/law stating that the equipment connected needs to be listed before I wasted time unhooking and hooking the equipment up.