Was on a co-workers job today where the inspector came because we were looking for a temp meter release for power on the building. Got a Tap box, CT cabinet, (2) metal troughs mounted outside. Out of the trough(service leaving the CT Cabinet) are parallel 3" PVC conduits with 4-500 MCM AL in them that pipe 30' and then enter a MB 600A 480V panelboard. Now the metal troughs are bonded with a 2/0 CU wire from the main panelboard inside. The bond wire is in a 1" pvc conduit. The inspector is citing 300.3(B) (2005NEC). Saying we need to have a ground wire in each and has to be with circuit conductors. I argued that its a "Bond" wire not a "Ground" wire and didn't need to be in the parallel conduits. Is he correct?????