250.50 Grounding Electrode System
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist , one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
If your water pipe exist as described then the connection requirements are mandatory -- new construction usually has a concrete encased electrode (footer steel) just because the electrical contractor forgets to or ignores to prepare does not mean it should be excluded -- no ground rods needed with footer steel.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist , one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
If your water pipe exist as described then the connection requirements are mandatory -- new construction usually has a concrete encased electrode (footer steel) just because the electrical contractor forgets to or ignores to prepare does not mean it should be excluded -- no ground rods needed with footer steel.