When you use the water pipe for grounding, the connection needs to be within the first 5' of where it enters the building. If you are bonding the water system, then the connection can be anywhere on the system and simply must be accessible. Here we require a Ufer or the two ground rods and then just bond the cold water.
The reason we only make you bond the cold water is because I don't know if there is 10' of copper in the ground or if it's been changed to plastic. In a neighboring jurisdiction the make you tie in within the first five feet, but they also have you run a jumper from the cold, to the hot, to the gas line. Why I don't know, because you have bonded the hot and the cold at all of the mixing valves and there is the exception for the gas line if you have plugged in gas appliances.
The reason we only make you bond the cold water is because I don't know if there is 10' of copper in the ground or if it's been changed to plastic. In a neighboring jurisdiction the make you tie in within the first five feet, but they also have you run a jumper from the cold, to the hot, to the gas line. Why I don't know, because you have bonded the hot and the cold at all of the mixing valves and there is the exception for the gas line if you have plugged in gas appliances.