from my understanding is that unless you have mc or conduit ran to your first receptacle. that is the only time you can use a afci receptacle. The reasoning behind it is it would leave the home run unprotected.
406.4(D)(4)(1) allows an AFCI receptacle for replacements.

406.4(D)(4) Arc-Fault Circuit-Interrupter Protection. Where a receptacle outlet is located in any areas specified in 210.12(A) or (B),
a replacement receptacle at this outlet shall be one of the following:
(1) A listed outlet branch-circuit type arc-fault circuit-interrupter receptacle
(2) A receptacle protected by a listed outlet branch-circuit type arc-fault circuit-interrupter type receptacle
(3) A receptacle protected by a listed combination type arc- fault circuit-interrupter type circuit breaker
 

mwm1752

Senior Member
Location
Aspen, Colo
from my understanding is that unless you have mc or conduit ran to your first receptacle. that is the only time you can use a afci receptacle. The reasoning behind it is it would leave the home run unprotected.
406.4(D)(4) give you direction and options to choose which AFCI protection method for replacement only - it states "receptacle outlet located in any areas specified in 210.12(A), (B), or (C)" does not say use the restrictions provided for those areas - IMO an AFCI receptacle is compliant in every replacement if chosen.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Right. IMHO the method restrictions for the run from panel to first box, where the AFCI will be located, apply only to new circuits subject to AFCI requirements, not to device replacements or circuit extensions that trigger an AFCI requirement.

Sent from my Pixel 4a using Tapatalk
 
Last edited:

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Would this section also apply to lighting additions if so how would you handle AFCI for that? Back to the panel or add an AFCI receptacle?
 

kwired

Electron manager
Location
NE Nebraska
I believe a new circuit
Would this section also apply to lighting additions if so how would you handle AFCI for that? Back to the panel or add an AFCI receptacle?
Yes it does and yes those are about your only choices unless they make a "blank face" AFCI that mounts in a device box like they do with GFCI's.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Or, mount one or several feed-through devices in boxes at the panel.
I was wondering about that, thought that might be an option just never tried to get that past. Would that also work for a mwbc past point of split in to 2 separate neutral?
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
This section of the codes still seems to be highly questioned or debated (even by inspectors). I heard that there was language added to the 2020 that was supposed to clear up some of the (mis)interpretations made by many of this section. Is that true? I don't have a 2020 to compare with, NYS just went 2017. Perhaps someone with access can share the wording from 2020 that supposedly makes it clearer. Or was that just a rumor?
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
This section of the codes still seems to be highly questioned or debated (even by inspectors). I heard that there was language added to the 2020 that was supposed to clear up some of the (mis)interpretations made by many of this section. Is that true? I don't have a 2020 to compare with, NYS just went 2017. Perhaps someone with access can share the wording from 2020 that supposedly makes it clearer. Or was that just a rumor?
Nobody on 2020? Or was there no changes?
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
Nobody on 2020? Or was there no changes?
The 2020 Code still gives you the 6 methods which you can protect a circuit, but like earlier additions, your best option is just to supply a new afci breaker.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
The 2020 Code still gives you the 6 methods which you can protect a circuit, but like earlier additions, your best option is just to supply a new afci breaker.
I was curious as to what language had changed to clear some of the confusion about AFCI requirements, what I had heard was that the elements of the section was not changed but the language did to clarify the interpretation of the section of code. Or was I misinformed?
 

kwired

Electron manager
Location
NE Nebraska
I was curious as to what language had changed to clear some of the confusion about AFCI requirements, what I had heard was that the elements of the section was not changed but the language did to clarify the interpretation of the section of code. Or was I misinformed?
One thing that did change relates to the 6 foot extension that doesn't require upgrading to AFCI - it says that six feet doesn't include conductors inside boxes or cabinets - or something to that effect. So when moving a panel you don't need to change to AFCI's if cable sheath added is no more than six feet.

Before it could be interpreted that if you had say 1.5 feet of free conductor in the old panel that you used as a splice box and had 2 feet of conductor in the new panel you could only relocate the new panel up to 2.5 feet away, now it is clear it can still be full six feet away even with additional conductor in the boxes/cabinets.
 

ccokz615

Member
Location
Tennessee
I believe some of the wording is if extending more than 6' or modifying the circuit arc fault required. Isn't extending the circuit 5' modifying the circuit???

Does the 2020 NEC give a definition of modify? My NEC doesn't but, I don't have access to a 2020 codebook. I can see the wording being interpreted in multiple ways as well. They need to define "modify" in the NEC I think, for clarity.

If I were reading this, I would assume that as long as I didn't add or remove anything from the original circuits design and didn't extend its point of utilization by 6' or more, then I wouldn't need to bring an existing circuit up to current code.

Example: Existing circuit = 6 receps, 20 amp, #12 AWG and no EGC.

As long as all I did was change out the receptacle's or replaced wiring with newer wiring (12-2) and the replacement components had the same attributes as the original then, I wouldn't have extended or modified the circuit in anyway other than, added an equipment ground.

The circuit would still have all of the receps located in the same spots with, the same amount of receps, fused at the same current rating being conducted by a wire with the same ampere rating as before. All I would have done was change out old components with, new components and stuck with the original circuit by design.

The addition of the EGC would be the catch. As long as the NEC clearly defines "Modify" then it makes it pretty simple to me.
 

jap

Senior Member
Occupation
Electrician
As long as all I did was change out the receptacle's or replaced wiring with newer wiring then, I wouldn't have extended or modified the circuit in anyway other than, added an equipment ground.


210.12(A) of (B), where branch-circuit wiring is modified, replaced, or extended, the branch circuit shall be protected by one of the following:
(1) A listed combination-type AFCI located at the origin of branch circuit......

I would say you modified the circuit by replacing the circuit wiring which is in the wording of the rule.

JAP>
 