Log # 1214-2
19-46-(550-24, Exception-(New): Reject
SUBMITTER: Bill . Shanks, Perrysburg, OH
RECOMMENDATION: Add:
Exception: Aluminum or copper-clad aluminum without
individual insulation where part of a cable assembly,
or bare copper, shall be permitted for the equipment
grounding conductor, when installed in a raceway for
permanent installation.
SUBSTANTIATION: As an inspector, I see this all the
time in mobile home parks. I feel this is just as safe
as an installation. The integrity of the equipment
ground is still maintained and protected from physical
damage.
It's very hard to tell an owner to take this out and
put in an INSULATED equipment ground when it serves the
same purpose.
PANEL ACTION: Reject.
PANEL COMMENT: A bare equipment conductor would
provide multi paths for fault currents. Ground
continuity is very critical because of nature of
structure.
Insulation reduces arcing between equipment grounding
conductor and other grounded equipment during a fault
condition.
Integrity of grounding conductor is preserved by
being insulated.
VOTE ON PANEL ACTION: Unanimously Affirmative.
19- 47 - (550-24): Accept
SUBMITTER: CMP 19
RECOMMENDATION: Revise Section 550-24 to read:
"Mobile home feeder conductors shall consist of
EITHER a listed cord, factory-installed in accordance
with Section 550-5(b) or a permanently installed feeder
consisting of four continuous, insulated, color-coded
conductors which shall be identified by the factory or
field marking of the conductors in compliance with
Section 310-12. "Equipment grounding conductors shall
not be identified by stripping the insulation." (Added
material in quotations.)
SUBSTANTIATION: To clarify that the feeder to a mobile
home is intended to be either a listed supply cord or a
permanently installed feeder and not both, Also to
clarify that it is not the Panel's intent to permit
bare equipment grounding conductors or to have the
insulation stripped to identify the conductor.
PANEL ACTION: Accept.
VOTE ON PANEL ACTION; Unanimously Affirmative.