I just dont get the DC disconnect in the inverter for lots of reasons;
First the NEC 690 has so many defined circuits to dance around it:
- 'PV source circuits'
- and the 'PV Output circuit'
- and the all encompassing 'PV system DC circuit'
I think of these as DC taps or 'service conductors' as they can get their protection at the 'load' end (inverter) or no over-current protection at all [690.9(1)]
I have been on more than a dozen PV inverter swap out service calls where its impossible for one man to swap, I'll admit I can't lift what I used to in my 20's, but those inverters are tanks, they could loose a few pounds and shed the DC disconnect.
Then on said service call the DC disconnect is built into the 'high voltage' device (inverter) you need to safety off to service.
While its unlikely the rotary switch has melted and cracked and will arc when I take the cover off, I have no idea till i do, I am there because the inverter "quit working and smells funny in the garage".
I cant lockout the thing I am removing /opening.
300V - 1000V DC per lockout tag-out policy involves going on a roof and unbolting PV panel(s) and unplugging wires...
For both those reasons I think it would make sense to have the DC disconnect (rotary switch if you will)
at the point of transition from the 'PV source circuits' and the 'PV Output circuit', then you could simplify the code and end article 690 at that DC disconnect, delete 'PV system DC circuit' and 'PV Output circuit' and you just now have a article 215 feeder from the DC disconnect/AFCI/GFCI/rapid shutdown device to the article 705 inverter or Article 408 DC panel:
PV Panel(s) ------- source circuit(s) ----->/----> DC disconnect / rapid shutdown / G/AFCI ----->'PV output circuit' (becomes DC feeder).
Once the DC disconnect is part of the rapid shutdown box (ahead off the shutdown relays) and 'accessible' per NEC at the edge of roof installs so, if you need to replace an inverter (or rapid shutdown box) you just need a ladder pop up to the edge of the install and flip a rotary switch.
If a siding guy damages the DC feeder conduit, pop up to the roof flip a switch.
Just my two cents