We need to perform an acceptance test on a 5kV 6500hp wound rotor motor. I plan on using a 5000V megger and performing a PI test and comparing the 10min and 1min values.
What is an acceptabalbe or minimum PI value I should see for this size/type motor?
Mhat is the minimum IR value in Megaohms I sould see for this motor?
Aside from testing the stator windings do I need to perfrom a seperate IR, or PI test on the rotor windings of this wound rotor motor?
I notice that our engineering spec for the project calls for Hi-Potting of all the 5kV motors. I believe it calls for 11kV DC for 1 min with a minimum IR value of 25Mohms. What are thoughts or standards on this Hi-Pot test for these 5kV motors? Good idea / bad idea? Are these standards correct?