Here it is Louis.
I could only get one attachment on this post.The other will follow.
-----Original Message-----
Sent: Wednesday, November 07, 2007 7:21 AM
To: louis duke
Subject: Re: FW: T&B Flag and Tee Connectors for Use in Grounding
andBonding Applications
Louis,
Thank you for the information. I have been traveling quite extensively
and am not sure if you ever received all the samples you needed. If
there was something missing, just remind me. The below is good news and
makes any transition design fairly easy as we worked with UL for listing
of the products for any field constructable design. I have attached some
information that may be helpful and also, the next phase of our KUBE
family of versatile products.
Regards,
jerry
Jerry A Woodward
>>> "louis duke" 11/6/2007 5:26 PM >>>
Hi Jerry, see below. Louis
Subject: T&B Flag and Tee Connectors for Use in Grounding and Bonding
Applications
Hi Louis,
It was good to meet you at the Southwestern Section IAEI meeting. Sorry
for the delay in responding to your question.
Based on the revision in Section 250.8 of the 2008 NEC, it appears that
it was the intent of NEC Code Making Panel 5 to permit any Listed
pressure connectors for grounding and bonding applications, and not only
pressure connectors specifically Listed for grounding and bonding.
At present, pressure connectors are covered in the UL product category
for wire connectors (ZMVV) and are not subject to the same testing as
grounding and bonding equipment (UL 467 - product category KDER).
Because on the 2008 NEC revision, we expect that we may receive
proposals to revise the requirements for pressure connectors to include
testing currently conducted only on grounding and bonding equipment. As
I am not aware that we have received any proposals yet, it would take
some time before any proposal would be adopted and become effective.
In the meantime, you may encounter different opinions based on the
applicable edition of the NEC that is in use. If using the 2005 or
earlier editions of the NEC, UL's position would be that Listed
grounding and bonding equipment (Product Category KDER) should be used
for 250.8 applications. For those using the 2008 edition of the NEC, all
Listed pressure connectors would be considered suitable.
Please note that these statements are the opinion of the writer, and
that formal interpretations of the NEC can only be made by the National
Fire Protection Association (NFPA).
Please contact me if you would like to discuss further.
Rich
Rich Berman
Sr. Staff Engineer
Regulatory Services
Underwriters Laboratories
333 Pfingsten Road
Northbrook, IL 60062
- For more information about UL, its Marks, and its services for
EMC, quality registrations and product certifications for global
markets, please access our web sites at
http://www.ul.com and
http://www.ulc.ca or contact your local sales representative. --
Attached Message
Attachment 1: GM-8103%20Multi-Tap_r2.pdf (application/pdf)