Irrigation pump in lake

I understand that,,, was merely making it a point we have used it on long circuits, the protection is a hedge against drop.
Making a point about "we have done it without issues" does not provide a lot of assurance considering the labor an material that will be involved.
 
When did gfci come in resi? Seems to me I have seen it in 70s,,, about 76 as breaker added to mobile for kitchen circuit. I remember early on the continuous talk a (and some bitchin) about the requirements from water etc.
 
When did gfci come in resi? Seems to me I have seen it in 70s,,, about 76 as breaker added to mobile for kitchen circuit. I remember early on the continuous talk a (and some bitchin) about the requirements from water etc.
What does that have to do with the conversation at hand?
 
What do uou think he should do and woiuld it be a deal killer if he had to comne back and add 2 space at the end or should we what if,f,,, just in case,,, and toss money at something probably never be an issue.
 
What do uou think he should do and woiuld it be a deal killer if he had to comne back and add 2 space at the end or should we what if,f,,, just in case,,, and toss money at something probably never be an issue.
We can address that if there is a problem. It may work out and hopefully it does but making him aware of the possibility of nuisance tripping being a real issue is proper.
 
As to the GFCI, they don't usually do well on runs that long. There will be a lot of nuisance tripping.
Depends on the brand. Square D says 250-300ft I believe.

An argument could be made for keeping with 120V and having a GFCI breaker at the source, because it would allow a 6” deep trench for the PVC, instead of 18”. If you are using a trencher though, it doesn’t make much difference.
 
Depends on the brand. Square D says 250-300ft I believe.

An argument could be made for keeping with 120V and having a GFCI breaker at the source, because it would allow a 6” deep trench for the PVC, instead of 18”. If you are using a trencher though, it doesn’t make much difference.
I was more talking about cumulative leakage along the way. A tiny leak so small it wouldn't cause a trip, but several added together would. I quit installing GFCI breakers protecting loads a good distance away after a few call backs for tripping. Luckily these were 120V loads and I could put GFCI receptacles at the load.
 