Irrigation pump in lake
I understand that,,, was merely making it a point we have used it on long circuits, the protection is a hedge against drop.
Making a point about "we have done it without issues" does not provide a lot of assurance considering the labor an material that will be involved.
When did gfci come in resi? Seems to me I have seen it in 70s,,, about 76 as breaker added to mobile for kitchen circuit. I remember early on the continuous talk a (and some bitchin) about the requirements from water etc.
What does that have to do with the conversation at hand?
What do uou think he should do and woiuld it be a deal killer if he had to comne back and add 2 space at the end or should we what if,f,,, just in case,,, and toss money at something probably never be an issue.
We can address that if there is a problem. It may work out and hopefully it does but making him aware of the possibility of nuisance tripping being a real issue is proper.
As to the GFCI, they don't usually do well on runs that long. There will be a lot of nuisance tripping.
Depends on the brand. Square D says 250-300ft I believe.
An argument could be made for keeping with 120V and having a GFCI breaker at the source, because it would allow a 6” deep trench for the PVC, instead of 18”. If you are using a trencher though, it doesn’t make much difference.
I was more talking about cumulative leakage along the way. A tiny leak so small it wouldn't cause a trip, but several added together would. I quit installing GFCI breakers protecting loads a good distance away after a few call backs for tripping. Luckily these were 120V loads and I could put GFCI receptacles at the load.
It's conceivable that you could have longer runs with 240V than 120V without tripping a GFCI. That's because the L1-G and L2-G voltages are 180 degrees out of phase, and so equal leakage currents from L1 and L2 to ground could cancel out and have a net leakage to ground close to zero. For example, if the two wires have an equal capacitance to ground, then the currents through these capacitances would be at the same level but 180 degrees apart. And so the common mode current that is measured by a GFCI would be zero. But if the leakage is only on one of the lines L1, L2, then there will be no cancellaton occurring.
... As to the GFCI, they don't usually do well on runs that long. There will be a lot of nuisance tripping. It's better to put them at the load end. A small panel at the load, and a GFCI breaker there. Since you only have 12-2 to work with, you would need to run a 12-3 so you could send a neutral to the panel. The load itself doesn't need the neutral, but the GFCI does to power the electronics in it.
You could use a small neutral forming transformer (such a a center-tapped 240V transformer winding) to create a neutral just to power the electronics of a GFCI at the load end of the run. But it's questionable whether it would meet the GFCI manufacturer's written requirements. It would create "a" neutral, but it would not be a grounded conductor.
Simple enough to make one or am I missing something?
Technically it should work fine. It's just a question of whether an inspector would understand it and approve it.
The transformer makes it a SDS. Add to ground rods and all should be good.